Quick Answer
Your East Penn 6V AGM batteries likely sustained some damage from the complete discharge to 8V, but your charging behavior suggests they may have recovered reasonably well. The key indicators are how they hold voltage under load and their actual capacity.
Tools & Parts Needed
The Quick Answer
Your six East Penn 6V AGM house batteries have likely suffered some damage from being completely discharged to around 8V, but they may still be recoverable. The fact that they're accepting charge and holding voltage reasonably well (only dropping 0.1V overnight) is actually encouraging. AGM batteries can typically survive one or two deep discharge events, but repeated deep cycling will permanently reduce their capacity. The charging behavior you're seeing - progressing from bulk to float to absorb - suggests your Magnum charger is working correctly and the batteries are responding, though they may have lost some of their original capacity.
What's Causing This
Deep discharge damage occurs when AGM batteries are drained below 50% of their capacity, and yours went much further - down to around 8V indicates they were nearly completely depleted. When AGM batteries sit at such low voltages for 2.5 weeks, the lead plates begin to sulfate heavily, which reduces capacity and can make them harder to charge. The repair shop should have disconnected your battery switch, as even minimal parasitic loads (like CO detectors, propane leak detectors, and inverter standby power) can drain batteries over time.
The good news is that your batteries are showing positive signs. The progression from bulk charging at 13.0V to float at 13.2V, then jumping to absorb at 14.2V when you reconnected, indicates the charger is reading the batteries' state correctly. AGM batteries typically need 14.1-14.4V for proper charging, so your Magnum's 14.2V absorb voltage is appropriate. The minimal voltage drop overnight (12.7V to 12.6V) suggests the batteries aren't heavily sulfated yet.
Tools You'll Need
- Digital multimeter capable of reading DC voltage accurately
- Battery conductance tester (hydrometers cannot be used on sealed AGM batteries)
- Battery load tester or carbon pile tester capable of testing 6V batteries
- Insulated wrenches and safety equipment
- Battery terminal cleaner and protectant spray
- Desulfating battery charger (if regular charging doesn't fully restore capacity)
- Notebook to record voltage readings and charging times
Step-by-Step Fix
- Continue the current charging cycle and monitor closely. Let your Magnum charger complete its full cycle - it should go from absorb charging back to float mode when the batteries reach full charge. This typically takes 12-24 hours of absorb charging for deeply discharged AGMs.
- Once in float mode, disconnect shore power and measure each battery's voltage individually using your multimeter. Healthy 6V AGM batteries should read 6.2-6.3V when fully charged and rested. Any battery reading significantly lower (below 6.0V) may have permanent damage.
- Perform a load test on each battery after they've rested for at least 2 hours without charging. Apply a 75-amp load for 15 seconds to each 6V battery - voltage should not drop below 5.1V during the test. If any battery fails this test, it needs replacement.
- Check your parasitic draw with all systems off and the battery switch on. Disconnect the negative battery cable, set your multimeter to DC amperage mode, and connect it between the negative cable and negative terminal. Draw should be less than 200 milliamps (0.2 amps) total for your setup. Higher draw means something wasn't turned off properly at the shop.
- Monitor battery performance over the next few weeks. Fully charge the batteries, then measure voltage daily to see how quickly they self-discharge. Healthy AGM batteries should only drop 0.1V per week maximum when not in use.
- If batteries show continued poor performance, consult your battery manufacturer's specifications before attempting any equalization, as most AGM manufacturers advise against equalization charging which can damage AGM batteries.
When to Call a Pro
Contact a professional battery specialist or RV technician if individual batteries are reading below 6.0V after charging, if any battery fails the load test, or if the batteries continue to lose more than 0.2V per day when not in use. These symptoms indicate permanent sulfation damage that requires battery replacement. Also call a pro if your parasitic draw exceeds 0.5 amps, as this suggests an electrical fault that needs professional diagnosis.
Consider professional help if you're uncomfortable performing load testing, as improper testing can be dangerous with large battery banks. A battery specialist can also perform capacity testing to determine exactly how much capacity you've lost, helping you decide whether replacement is economically justified. Given that quality 6V AGM batteries like your East Penn units cost $200-300 each, professional testing might save you money by identifying which specific batteries need replacement rather than replacing the entire bank.