Quick Answer
ME2012 showing 50A fault, self-test failure, and breaker trips indicates internal inverter failure or ground fault. Disconnect inverter to test shore power separately. Check all connections. Likely needs professional repair or replacement.
Tools & Parts Needed
The Quick Answer
Your ME2012 inverter in your Monaco Cayman is showing classic signs of an internal fault that requires a proper reset sequence, not just a simple power cycle. The 50-amp reading on your remote console combined with the self-test connection flashing and fault light behavior indicates the inverter is detecting an overcurrent condition or internal component failure. The shore power breaker tripping confirms there's likely a short circuit or ground fault within the inverter itself. You're absolutely right that this needs a fault reset, but it requires following the specific ME2012 reset procedure outlined in your manual - simply turning it off and on won't clear these types of faults.
What's Causing This
The ME2012 inverter is experiencing what Magnum Energy calls a "hard fault" condition. The 50-amp current reading displayed suggests the inverter is either detecting or actually drawing excessive current. When the self-test sequence runs and flashes multiple times before showing the fault light, it's cycling through its internal diagnostics and finding problems with either the power switching components, the transformer, or ground fault detection circuits.
The shore power breaker tripping is particularly concerning because it means the fault is severe enough to affect the AC input side of the inverter. This could be caused by failed MOSFETs in the inverter section, a shorted transformer winding, or problems with the transfer relay system. The fact that your batteries aren't charging indicates the charger section of the inverter has also shut down due to the fault condition.
These symptoms together point to either internal component failure or a cascading fault where one problem triggers protection circuits throughout the unit. The ME2012 has multiple fault codes stored in memory that need to be properly cleared using the reset sequence, not just powered down.
Tools You'll Need
- Digital multimeter capable of reading DC and AC voltage
- Non-contact voltage tester for safety verification
- Screwdriver set (Phillips and flathead)
- Wire brush or contact cleaner for battery terminals
- Safety glasses and insulated gloves
- Your ME2012 owner's manual (critical for the exact reset procedure)
- Flashlight or headlamp for working in electrical compartments
- Camera or phone to document wire connections before disconnection
Step-by-Step Fix
Safety First: Turn off all breakers to the inverter and verify no power is present with your non-contact tester before beginning any work.
- Perform the ME2012 Hard Reset: Turn the AC input breaker OFF first, then locate the inverter's main DC disconnect and turn it OFF. Wait per the timing specified in your ME2012 manual. After power is restored, press and hold the inverter's ON/OFF button on the remote panel for 15 seconds to initiate the reset sequence per manufacturer procedure.
- Check All Connections: Inspect and clean all DC battery connections to the inverter, looking for corrosion, loose bolts, or damaged cables. Check the AC output connections and ensure the transfer switch connections are secure. Document any wire positions with photos before disconnecting anything.
- Measure Battery Voltage: With your multimeter, verify battery bank voltage is between 12.0-12.8V for 12V systems or 24.0-25.6V for 24V systems. If voltage is below 11.5V (12V) or 23V (24V), charge batteries with an external charger before proceeding.
- Restore Power Gradually: Turn the AC input breaker back ON first, then wait 30 seconds. Turn the DC disconnect back ON. The inverter should begin its startup sequence. Watch the remote display carefully for fault codes during the self-test.
- Monitor the Reset Process: The ME2012 will display fault codes if they're still present. Watch for fault codes during diagnostics - specific codes and meanings are listed in your ME2012 manual. Internal hardware fault codes indicate requiring professional service.
- Test Operation: If no fault codes appear, first verify the inverter shows normal standby operation with no load, then test with a small load (like a 100W light bulb). Then test the charger function by monitoring battery voltage - it should rise to the appropriate charging voltage per your battery type (see manufacturer specs for both inverter and battery requirements).
When to Call a Pro
If the hard reset procedure doesn't clear the fault codes and the shore power breaker continues to trip immediately upon restoration, you're dealing with internal hardware failure in the ME2012. Fault codes "06" (inverter fault) or "07" (charger fault) specifically indicate component-level problems that require bench repair or unit replacement. Don't keep attempting to reset a unit that trips the shore power breaker - this can damage your RV's electrical system or create fire hazards.
Call a certified Magnum Energy service center if you see persistent fault codes after the reset, if the unit shows normal displays but still won't produce power, or if you measure unusual voltages during your testing. The ME2012 inverter typically costs $800-1200 to replace, while professional repair services range from $200-500 depending on the failed components. Given the age of Monaco Cayman RVs, it may be more cost-effective to upgrade to a newer inverter with better diagnostic capabilities and warranty coverage.
Help us improve this article by flagging technical issues or inaccuracies.